Details on "Air Pollution Proc. 1" (Room Level)

Information on the Air Pollution Method 1 section of the Ventilation module in LINEAR Building.

In this area, you configure the room-specific settings for determining the required air volumes for rooms in non-residential buildings based on the calculation method DIN EN 16798-1 Air Pollution, Method 1 (03-2022).

You are here

Module OverviewVentilationRoom Level (Building Structure)Air Pollution Proc. 1

“Air Pollution Method 1” section of the Ventilation module in LINEAR Building.

General Room Data

The room number, the room name and the room temperature for the heating or cooling mode are displayed on the left-hand side, which you can adjust as required. Depending on the module, you can use the button to the right of the room temperature to open the Temperatures dialog, in which you can select the temperature variables stored in the master tables and create new temperature variables.

The area resulting from the clear internal dimensions and the clear internal dimensions of the room are displayed in brackets in the right-hand area.

: Opens the Room Data dialog in which you can adjust the parameters of the room.

General

Category: Drop-down list for selecting the category of expectations for the quality of the indoor climate in accordance with DIN EN 15251. The higher the expectations, the greater the volume flow rates required to ensure the desired indoor climate quality. If the category was taken from the global default settings at project level, it is given the addition From Project Settings:.

Building Emission: Drop-down list for selecting the pollutant load of the building according to DIN EN 16798-1. The higher the pollutant load in a building, the greater the volume flow rates required to reliably dissipate or dilute the loads. If the setting was adopted from the global default settings at project level, it is given the addition From Project Settings:.

Number of Persons

Defines the number of people in the room. Manual changes to the number of people at this point have no effect on the number of persons in the general room data. Click on the button to reset the number of people from the general room data. If the general occupancy is displayed, this is indicated by the entry P (e.g. "P = 0.75").

Person-related Specific Outdoor Air Volume Flow Rate

Defines the specific outdoor air volume flow rate per person.

: One click restores the value from the global default settings.

Building-related Specific Outdoor Air Volume Flow Rate

Defines the building-related specific outdoor air volume flow rate per square meter.

: One click restores the value from the global default settings.