Details on System Preselection

Information on the area System Preselection of the modulesPanel Heating/Panel Cooling.

In the System preselection, select a desired panel heating systems in the System selection section and add the selection to your project. Added systems are listed in the Systems section, where their System parameters... and system-dependent Screed additives... can also be set. In addition, in the System preselection section, General default settings, settings for the Project variables and settings for Quick dimensioning can be defined.

You are here:

Module OverviewRadiant Heating/Radiant CoolingProject LevelSystem Preselection

Radiant Heating System Preselection Linear Building

System selection

In the System selection area, select the manufacturer, the system group, the system and pipe type to be dimensioned to add them to the preselection of your project.

Use the Floor/ceiling/wall buttons to define the position of the system in the room.

Note:

Not every manufacturer offers ceiling and wall systems.

Editing the preselection of systems

Use the button to transfer the selected system to the Systems field. The system is now in the preselection and is available for dimensioning in the current project. During the project editing you can add additional systems for preselection.

Use this button to remove a selected system from the preselection in the Systems field. This is only possible if the system is not used in the project. If a system that is no longer in use cannot be removed, click one of the message buttons in the symbol bar. The project will be recalculated and you can then remove systems that are no longer used.

Systems

Displays the systems assigned to the project and allows settings to be made for the system parameters and screed additives of the respective system. If the Screed additives... button is deactivated, there are no screed additives for the selected system.

Project Variables

The buttons Temperatures, R-Values and Room templates open the corresponding dialogs in which the master tables belonging to the variables can be edited.

General Default Settings

Determines the default settings for designing all of the project’s systems.

Design Supply Water Temperature

Defines the design supply water temperature to be used as the basis for calculation.

The button is displayed only for radiant heating systems and opens the Supply Water Temperature Design dialog, where the design supply water temperature can be calculated using all relevant parameters.

Min. Differential Temperature

Defines the desired minimum differential temperature between supply and return water temperature.

Note:

The room temperature is automatically considered as the minimum possible return water temperature and will not fall below it.

Max. Differential Temperature

Defines the desired maximum differential temperature between supply and return water temperature.

Valve Setting

Defines the calculation case the valve setting is shown for. Displayed are only those options for which the manufacturer provides the system.

Table 1. Description of the Valve Settings

Valve Setting

Description

Only for Heating

The optimum balancing of the required throttle resistances of the heating circuits via the control valves/volume flow controllers is only carried out for the heating case.

The optimal operation for cooling in summer cannot be guaranteed. This may lead to restrictions in comfort.

Mixed Mode

The optimal balancing of the required throttle resistances of the heating circuits via the control valves/volume flow controllers is achieved as an optimal combination between heating and cooling.

Each valve is checked for the required setting value for the heating case as well as for the cooling case. The valve setting with the lowest pressure loss is assigned to the valve.

It is guaranteed that in normal projects there are no comfort restrictions.

This method is based on the assumption that the room controllers, in connection with the actuators, ensure the necessary residual throttle resistances for a hydraulically balanced pipe network, regardless of the season.

Note:

In mixed mode the system is not hydraulically balanced. The required power supply has to be ensured by the closed loop control system.

Mixing Mode - Priority Heating

The optimal balancing of the required throttle resistances of the circuits via the control valves/volume flow controllers is carried out as mixed mode with a preference for the heating case.

Note:

In mixed mode the system is not hydraulically balanced. The required power supply has to be ensured by the closed loop control system.

Mixing Mode - Priority Cooling

The optimal balancing of the required throttle resistances of the circuits via the control valves/volume flow controllers is carried out as mixed mode with a preference for the cooling case. case.

Note:

In mixed mode the system is not hydraulically balanced. The required power supply has to be ensured by the closed loop control system.

Limit Surface Temperatures...

The button opens the dialog Limit Surface Temperatures, in which the maximum permitted surface temperatures for the dimensioning of surfaces with systems are defined.

At least one manifold per apartment/storey

Enabled: A separate manifold is created automatically for each new apartment and each new floor.

Disabled: A new manifold is created if the maximum number of circuits is exceeded in the manifold used.

Identify Material in Detail

Enabled: A detailed listing of all components in the parts list is provided.

Disabled: In their parts lists, some manufacturers combine components into material packages.

Average Feed Pipe Length to Manifold (Supply-+ Return)

Defines the average length of the feed pipes from the heating circuit to the manifold at initial design. Add the pipe lengths of supply and return water pipe to the manifold.

Usually the heating circuits are dimensioned first, followed by the calculation of the feed pipe lengths to the manifold. The calculated values are entered in the room components table. When using the actual feed pipe lengths, the maximum pressure loss or the maximum circuit length may be exceeded. This can be avoided by specifying the average feed pipe length.

Quick dimensioning

Defines the setting for border zones in quick dimensioning.

Border Zones Always as Independent Circuit

Enabled: During quick dimensioning, the border zones are automatically created as independent circles with their own manifold connection.

Disabled: The border zones are created during the quick dimensioning as row-integrated border zones in the circles of the occupied zones.