In this area, configure the room-specific settings for determining the required air volumes for rooms in non-residential buildings based on the calculation method VDI 2052-1 Kitchens (04-2017). Values conforming to the guidelines are stored as default values.

You are here

Module OverviewVentilationProject, Building Part, Storey, Area Level (Building Structure)Air VolumesCalculation Method …VDI 2052-1 Kitchens (04-2017) (Selection of Calculation Method)Room LevelKitchen

Area "Kitchens" in the ventilation module of LINEAR Building

General Room Data

The room number, the room name and the room temperature for the heating or cooling mode are displayed on the left-hand side, which you can adjust as required. Depending on the module, you can use the button to the right of the room temperature to open the Temperatures dialog, in which you can select the temperature variables stored in the master tables and create new temperature variables.

The area resulting from the clear internal dimensions and the clear internal dimensions of the room are displayed in brackets in the right-hand area.

: Opens the Room Data dialog in which you can adjust the parameters of the room.

Kitchen Type

Drop-down list to select the type of kitchen. For the different kitchen types, corresponding simultaneity factors, which you can adjust as required, are provided in connection with the kitchen names.

Kitchen Name

Defines the size of the kitchen. Which sizes are available depends on the Type of Kitchen. For the different kitchen sizes, corresponding simultaneity factors, which you can adjust as required, are provided in connection with the Kitchen Type.

Simultaneity Factor

Sets the simultaneity factor resulting from the Kitchen Type and Kitchen Name for the use of kitchen appliances. If necessary, you can adapt the value to the requirements of your project.
Note: Changes to the stored default values should only be made after detailed consultation between the operator, kitchen planner, and HVAC planner.

: One click restores the default value in accordance with the guidelines.

Flow Type

Drop-down list for defining the air flow pattern in the room, which is created by the introduction of supply air with air handling units. For the different flow types, guideline-compliant washout degrees are stored, which can be adjusted if necessary.

Degree of Rinsing

Specifies the flow-dependent washout degree for blocks under exhaust hoods and exhaust ceilings. If supply air or other air flows in the room disrupt the rising heat beneath the detection devices, the required airflow to capture the heat and substance loads increases. Thus, this factor considers how strongly the heat flow is influenced by air flows in the room. If necessary, the washout degree can be adjusted.
Note: The prerequisite for using the washout degree is that there are no cross-currents available in the room.

: One click restores the default value in accordance with the guidelines.

Areas: Exhaust Air Hoods, Exhaust Air Ceilings, Free-Standing Installations

In the tables in these areas, you create the blocks that contain the individual kitchen appliances. Click in an empty row or use F5 and select Kitchen Extract Air Hood or Kitchen Extract Air Ceiling or Free Installation in the context menu to create a new block. After opening the context menu again, the Appliance entry is available to add a line for a kitchen appliance to the block. You can then open the Table A1: Specific sensible and latent heat emission and moisture emission from kitchen appliances to the room dialog via the button in the row of the appliance. In this dialog, you can select different types of kitchen appliances for which default values for the heat and water vapor emission of the appliances to the room are stored from the directive. If you want to add further appliances to a block and the block is not the last block added, select the row with the block, press F5 and select Appliance in the context menu.

By clicking you have the possibility to copy the contents of the table with or without column heading and paste it into Excel.

If you have selected individual rows or cells, you can copy the selected data with the key combinations Ctrl+C (with column heading) or Ctrl+Shift+C (without column heading) and paste it into Excel, for example.

Column Description
Name

Defines the name of the block or appliances and allows appliances to be added. Changed appliance names are shown in bold. Remove changed appliance names to restore the original designation.

Clicking on opens the dialog Table A1: Specific Sensible and Latent Heat Emission and Moisture Emission from Kitchen Appliances to the Room, where you can select a type of kitchen appliance to apply the stored values for heat and, if applicable, water vapor emissions of the appliances to the room. You can adjust the transferred values as required.

Number

Always displays 1 for blocks and allows you to adjust the number of appliances in a block.

Length

Specifies the length of the block from which, together with the Width, the hydraulic diameter required for calculating the thermal volume flow of the block is determined. For blocks in which the z-values of devices vary, the hydraulic diameters of the individual devices are decisive for determining the thermal volume flow of the block and the dimensions of the individual devices are required.

Width

Specifies the width of the block from which, together with the Length, the hydraulic diameter required for calculating the thermal volume flow of the block is determined. For blocks in which the z-values of devices vary, the hydraulic diameters of the individual devices are decisive and the dimensions of the individual appliance are required.

Height

Defines the height of the block or appliance.

Hydraulic Diameter

Sets the hydraulic diameter of the block or device, determined from the Length and Width, which is required for determining the thermal flow of the block. You can adjust the values determined if necessary. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

z
Sets the height of extraction above the block. For free installation blocks, the distance to the nearest detection equipment that transfers the loads of the block must be specified.
Note: If a block contains devices with z-values that deviate from the z-value of the block, the thermal volume flow of the block is determined from the thermal volume flows of the individual devices. The dimensions of the individual devices are required to determine the thermal volume flows of the devices, as otherwise the hydraulic diameters of the devices cannot be calculated.
If a z-value of a device differs from the z-value of its block, the value is shown in bold. If necessary, remove the z-values shown in bold to restore the z-value of its block.
Arrangement of the Heat Source

Defines the position of the block in the room that influences the reduction factor r.

r

Sets the reduction factor dependent on the Arrangement of the Heat Source, which you can adjust if necessary. Values greater than 0 up to and including 1 can be entered. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

V_h

Enables application of an additional direct supply air volume flow for blocks under exhaust hoods, which is blown into the exhaust hood. This leads to a stabilization of the flow, as the induction effect of the supply air jet results in an improved extraction effect.

Operating Mode Defines the operating mode of the devices. If you have selected a kitchen appliance type in the dialog Table A1: Specific Sensible And Latent Heat Emission As Well As Moisture Emission From Kitchen Appliances To The Room, for which values are available for both electric or steam heating and gas heating, the values for heat and water vapor emissions to the room will automatically adjust when switching the operating mode.
Q_S Sets the sensible heat emission of the devices to the room. From the sensible heat emission and the connection power P, the Sensible Heat Load Q_S_K is determined, taking into account the convection proportion. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.
D Determines the water vapor output of the appliances to the room. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.
P Sets the connection power per appliance. From the connection power and the sensible heat emission Q_s, the Sensible Heat Load Q_S_K is determined, taking into account the convection proportion.
Q_S_K Displays the sensible heat load per device, which is determined based on the sensible heat emission Q_s and the connection capacity P, considering the convective portion.
V_th

Displays the thermal volume flow of the block. For blocks in which the z-values of appliances vary, the thermal volume flow rates of the individual devices are displayed.

V_erf

Displays the resulting extraction volume flow of the block required for complete heat and material extraction above the block.

Area: Dishwashers

In this table, you define the dishwashers in the room with its wash ware so that the heat emissions from the dishwashers and the wash ware are considered in the room during the determination of the air volume, and the required supply and exhaust air flow rates are calculated. Click in an empty line or use F5 and select Dishwasher in the context menu to add a dishwasher. After reopening the context menu, you can use the Wash Ware entry to add a row for wash ware to the dishwasher. You can then use the button in the wash ware row to open a context menu with various types of wash ware, for which guideline-compliant factors for the heat capacity of the wash ware (F_s) are stored. If you want to add more wash ware to a dishwasher and the machine is not the last machine added, select the line of the machine, press F5 and select Wash Ware in the context menu.

By clicking you have the possibility to copy the contents of the table with or without column heading and paste it into Excel.

If you have selected individual rows or cells, you can copy the selected data with the key combinations Ctrl+C (with column heading) or Ctrl+Shift+C (without column heading) and paste it into Excel, for example.

Column Description
Name

Defines the name of the dishwasher or the wash ware. Changed designations for wash ware are shown in bold. Remove changed wash ware names to restore the original designation.

opens a context menu in rows of wash ware with various types of wash ware for which guideline-compliant factors for the heat capacity of the wash ware (F_s) are stored.

Washing Procedure Determines the dishwasher's washing process. Different types of dishwashers are offered depending on the chosen washing process.
Dishwasher Type Specifies the type of dishwasher depending on the Washing Process. For the different types of dishwashers, a selection of corresponding suggested values for the hourly Standard Plate Capacity and the sensible heat release to the room Q_Machine is stored.
Standard Plate Capacity Specifies the hourly standard plate capacity of the dishwasher. Depending on the chosen Dishwasher Type, different suggested values are available.

: Opens a context menu with suggested values for the corresponding type of dishwasher.

Q_Machine Sets the sensible heat emission of the dishwashers to the room. Depending on the chosen Dishwasher Type, different suggested values are available.

: Opens a context menu with suggested values for the corresponding type of dishwasher.

T_Re Sets the temperature of the air entering the room. By default, 20 °C is set when adding dishwashers. Adjusted values are displayed in bold. If necessary, remove adjusted values to restore the default temperature.
T_Ra Sets the temperature of the air exiting the room. By default, 28 °C is set when adding dishwashers. Adjusted values are displayed in bold. If necessary, remove adjusted values to restore the default temperature.
n Sets the hourly amount of items to be washed (e.g., plates/hour or place settings/hour). This number, the factors F_s and f_A are used to determine the heat output of the wash ware to the room (Q_washware).
F_s Determines the factor for the heat capacity of the wash ware. This factor, the hourly number of wash items n and the cooling factor f_A are used to determine the heat transfer of the wash items to the room (Q_washware). Guideline-compliant default values are stored for the types of wash ware offered, which you can adjust as required. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.
f_C Defines the cooling factor of the wash ware. This factor, the hourly number of wash items n and the factor F_s are used to determine the heat transfer of the wash items to the room (Q_washware). Directive-compliant factors are stored for the different types of wash ware, which you can adjust as required. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.
Q_washware Shows the sensible heat emission of the wash ware to the room, which is determined from the factors F_s, f_A and the hourly number of wash ware n.
V_sup Indicates the required supply air volume flow.