Details on "Gymnasiums" (Project Level)

Information on the Gymnasiums section on room level of the Ventilation module in LINEAR Building.

In this area, configure the global settings for determining the required air volumes for rooms in non-residential buildings based on the calculation method DIN 18032-1 Gymnasiums (11-2014). In this section you will also find an overview of all rooms assigned to this calculation method, including their settings. You can edit the room settings in the overview on a room-by-room basis and across rooms by using the zb column.

You are here

Module OverviewVentilationProject/Building Part/Storey/Area Level (Building Structure)Air VolumesCalculation Method …DIN 18032-1 Gymnasiums (11-2014) (Selection of Calculation Method)Project LevelGymnasiums

“Gymnasiums” area on project level of the Ventilation module in LINEAR Building.

Outdoor Air Flow Rates

Volume Flow Rate per Athlete: Sets the global default setting for the required volume flow rate per person engaged in sports. You can adjust the standard-compliant default value if necessary. Changed values are displayed in bold.

: One click restores the standard default value.

Volume Flow Rate per Spectator: Sets the global default setting for the required volume flow rate per spectator seat. You can adjust the standard-compliant default value if necessary. Changed values are displayed in bold.

: One click restores the standard default value.

Air Exchange Rate ( Fitness, Strength Training and Martial Arts Rooms)

Minimum Air Exchange Rate: Sets the global default setting for the required minimum air exchange rate. You can adjust the standard-compliant default value if necessary. Changed values are displayed in bold.

: One click restores the standard default value.

Volume Flow Rate per Device Station: Sets the global default setting for the required volume flow rate per device station. You can adjust the standard-compliant default value if necessary. Changed values are displayed in bold.

: One click restores the standard default value.

Air Exchange Rate (Changing and Shower Rooms)

Minimum Air Exchange Rate Changing Rooms: Sets the global default setting for the required minimum air exchange rate for changing rooms. You can adjust the standard-compliant default value if necessary. Changed values are displayed in bold.

: One click restores the standard default value.

Minimum Air Change Rate Shower Rooms: Sets the global default setting for the required minimum air exchange rate for shower and sanitary rooms. You can adjust the standard-compliant default value if necessary. Changed values are displayed in bold.

: One click restores the standard default value.

Room Settings

This table shows all rooms to which the calculation method DIN 18032-1 Gymnasiums (11-2014) has been assigned and allows the editing of room settings.

By clicking you have the possibility to copy the contents of the table with or without column heading and paste it into Excel.

If you have selected individual rows or cells, you can copy the selected data with the key combinations Ctrl+C (with column heading) or Ctrl+Shift+C (without column heading) and paste it into Excel, for example.

Column Description
et

Defines which rooms are edited together. Tick the rows of the rooms that you want to edit together and then change the desired parameters for one of the rooms.

Clicking on the column header et activates or deactivates all rows.

Location

Shows the name and location of the room in the Building Structure. You can change the name if required.

Room Area

Displays the area of the room defined by the internal dimensions.

Room Volume

Displays the volume of the room defined by the internal dimensions.

Room Type acc. to DIN 18031-1

Defines the room type according to DIN 18031-1. Click on if necessary to assign a different room type.

n,Athlete

Defines the number of people exercising in the room.

n,Viewers

Defines the number of spectator seats in the room.

n,Device Test Sets the amount of device stations in the room.
V_Athlete

Determines the required volume flow rate per person exercising. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

V_Spectator

Defines the required volume flow rate per spectator seat. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

Minimum Air Exchange Rate

Specifies the required minimum air exchange rate in condition/strength training and martial arts training rooms. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

V_DeviceTest

Specifies the required volume flow rate per device station in condition/strength training and martial arts training rooms. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

Minimum Air Exchange Rate (Changing Rooms)

Specifies the minimum air exchange rate in changing rooms. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

Minimum Air Exchange Rate (Shower Rooms)

Specifies the minimum air exchange rate in shower rooms. Adjusted values are displayed in bold. Remove adjusted values to restore the original value.

V_tot

Displays the required total volume flow rate of the room. This value is transferred to the Air Volumes area as the result of the air volume determination.